I am laying out a VRF heat pump system for a six-storey office. The outdoor units sit on the roof and the farthest indoor unit is in the ground-floor reception. The catalogue lists several limits: total pipe length, longest pipe (actual and equivalent), length after the first branch, height difference between outdoor and indoor units, and height difference between indoor units.
- Which of these limits actually govern the layout?
- How do I calculate equivalent length?
- What do I do when one limit is exceeded, and does long piping reduce the capacity I selected?
November 10, 2026 at 9:55 am #5569MEP Center Engineering
KeymasterAll of the listed limits govern at the same time, and they are manufacturer- and model-specific: check every one against the data book of the exact outdoor unit, then apply the length and height capacity correction before you confirm the selection.
The limits to check
- Longest pipe, actual and equivalent – from the outdoor unit to the farthest indoor unit. Typical published values are in the range of 150-200 m actual and somewhat more as equivalent length.
- Length after the first branch – often about 40 m as standard, extendable (commonly up to about 90 m) only if the manufacturer’s conditions are met, such as upsizing certain pipes or limiting the difference between the nearest and farthest unit.
- Total piping length – sum of all liquid (or gas) pipe runs, typically several hundred metres up to about 1000 m on large systems.
- Height difference outdoor-indoor – usually different for outdoor unit above (often 50 m, more with options) and below (often 40 m).
- Height difference between indoor units – commonly 15-30 m. This is the limit most often forgotten on multi-storey buildings.
Equivalent length
Equivalent length = actual length + (number of elbows x equivalent length per elbow) + (branch kits x their equivalent length) + any other fittings listed by the manufacturer. Per-fitting values depend on pipe size; take them from the data book, not from water-pipe tables.
Worked example
Roof outdoor unit, 56 kW nominal (two equal 28 kW modules). Indoor units total 54 kW nominal, so the connection ratio is 54 / 56 = 96 %, within the 100 % maximum. Assumed data-book values: 0.5 m per elbow, 0.5 m per branch kit.
Check Design Example limit Result Longest equivalent: 118 m + 22 x 0.5 + 5 x 0.5 131.5 m 190 m OK After first branch 58 m 40 m (90 m with conditions) Check conditions Total piping 640 m 1000 m OK Outdoor above indoor 26 m 50 m OK Indoor to indoor 22 m 15 m Fails Two fixes are needed. The 58 m after the first branch is acceptable only if the extension conditions are satisfied; otherwise move the first branch closer to the far end of the system. The 22 m indoor-to-indoor height exceeds this model’s 15 m, so split the building into two systems by floor zone (or choose a model with a higher allowance).
Capacity: if the manufacturer’s correction chart gives, say, 0.90 for 131.5 m equivalent and 26 m height, the available cooling capacity is 56 x 0.90 = 50.4 kW. Compare that with the diversified block load of the zone, not with the sum of indoor nominal capacities. Do not fix a shortfall by raising the connection ratio above 100 %; select the next outdoor unit size, keeping the modules in a group equal or at most one step apart.
Common mistakes
- Checking only the longest run and ignoring indoor-to-indoor height.
- Using plan lengths without risers and drops.
- Forgetting that additional refrigerant charge grows with liquid pipe length, which then affects the room leak-concentration check.
- Applying one manufacturer’s limits to another manufacturer’s equipment at tender stage.
Related: VRF branch kit selection, 10 common VRF design mistakes. For deeper study: VRF/VRV system design course.
Check the edition of the code that applies to your project.
-