Aluminium vs copper cable: how do I size the cross-section?

Viewing 2 posts - 1 through 2 (of 2 total)
  • Author
    Posts
  • #5520

    Starter question — a frequently asked question posted by the MEP Center team to open this forum. Share your own experience below.

    A 400 V three-phase sub-main feeds a 100 kW panel at cos φ 0.9 over a 120 m route on a perforated cable tray. The contractor proposes aluminium XLPE cable instead of copper to cut cost.

    • How much larger does the aluminium cross-section need to be?
    • Is there a simple ratio, or must current-carrying capacity and voltage drop be recalculated?
    • What else changes with aluminium: short-circuit check, terminations, minimum sizes?

    A worked comparison with IEC 60364-5-52 and a note on NEC practice would help.

    #5521

    There is no fixed conversion ratio: size the aluminium cable from scratch with the same three checks as copper (current-carrying capacity after derating, voltage drop, short-circuit withstand). In practice aluminium ends up one to two standard sizes larger, roughly 1.4 to 1.7 times the copper cross-section.

    Why aluminium is larger

    • Resistivity at 20 °C: copper 0.0172, aluminium 0.0283 Ω·mm²/m, a ratio of about 1.64. For equal resistance (equal voltage drop) aluminium needs about 1.6 times the area.
    • For equal current-carrying capacity the ratio is smaller, because a larger conductor dissipates heat better. Tabulated aluminium ampacity is about 78 % of copper of the same size.
    • Short-circuit factor k (IEC 60364-5-54, XLPE): copper 143, aluminium 94, so the minimum size from S ≥ √(I²t)/k is about 1.5 times larger.

    Worked example (IEC 60364-5-52, method E, XLPE multicore)

    1. Design current: IB = 100 000 / (√3 × 400 × 0.9) = 160.4 A. Protective device In = 160 A.
    2. Derating: ambient 40 °C (0.91) × two circuits touching on perforated tray (0.88) = 0.80.
    3. Required tabulated current: It ≥ 160 / 0.80 = 200 A.
    4. From the method E table: copper 50 mm² is too small, copper 70 mm² passes; aluminium 70 mm² is too small, aluminium 95 mm² passes (about 182 A after derating, ≥ 160 A).
    5. Voltage drop, ΔU = √3 × IB × L × (R cos φ + X sin φ), with R at 90 °C and X ≈ 0.08 Ω/km:
    Cable R at 90 °C (Ω/km) ΔU (V) ΔU (%)
    Cu 70 mm² 0.342 11.4 2.85
    Al 95 mm² 0.410 13.5 3.37
    Al 120 mm² 0.324 10.9 2.72

    If your voltage-drop budget for this sub-main is 3 %, copper 70 mm² passes, aluminium 95 mm² fails and aluminium 120 mm² is the answer. Here voltage drop, not ampacity, governs the aluminium size. On long routes this is the usual result, and it is why a fixed ratio misleads.

    Short-circuit and other checks

    • Confirm S ≥ √(I²t)/k with the let-through energy of the actual MCCB, using k = 94 for aluminium XLPE.
    • The protective conductor of an aluminium cable has a higher impedance, so recalculate fault-loop impedance and disconnection time.
    • Aluminium is normally used only from 16 mm² upwards for fixed power circuits.
    • Terminations: use bimetallic (Al/Cu) lugs or terminals rated for aluminium, contact grease, and the manufacturer’s torque. Re-torque checks belong in the commissioning plan.
    • NEC practice: use AA-8000 series alloy conductors, take ampacity from the 75 °C column (NEC 110.14(C)), and make sure the equipment terminals are marked AL/CU.

    Common mistakes

    • Converting with a single “one size up” rule and skipping the voltage-drop check.
    • Checking the cable against IB and forgetting the In ≤ Iz rule for the breaker.
    • Gland, lug and busbar connections sized for copper. A larger aluminium conductor may not fit the breaker terminals without spreaders. See Cable Gland Selection and Cable Tray Sizing: Fill, Spacing and Derating.

    For deeper study: Electrical Power Systems Design course.

    Check the edition of the code that applies to your project.

Viewing 2 posts - 1 through 2 (of 2 total)