We are designing the ventilation for an enclosed underground car park of about 4000 m² with a clear height of 3.0 m. The architect prefers jet fans instead of ductwork, and the system must also serve smoke clearance in a fire.
- What airflow rates are used in European and US practice for normal (pollution) mode and fire mode?
- How should CO and NO₂ detection control the fans, and where are the sensors placed?
- What are the layout rules for jet fans and the main exhaust fans?
November 10, 2026 at 9:55 am #5563MEP Center Engineering
KeymasterSize the main exhaust for the fire or smoke-clearance case required by your code, run it at reduced speed under CO/NO₂ control in normal operation, and use jet fans only to move air towards the exhaust points. Normal-mode design is a dilution problem; fire mode is usually verified by CFD.
1. Airflow rates
- UK and many European practices: 6 air changes per hour for normal ventilation and 10 ach for smoke clearance (Approved Document B; BS 7346-7 for jet fan smoke control). Many national codes, including Turkey’s, follow similar figures; check yours.
- IMC 404 (US): 0.75 cfm/ft² (3.8 l/s·m²), with reduced operation permitted under CO and NO₂ detection control.
- ASHRAE Applications Handbook gives a contaminant-based method for CO dilution when the code allows it.
2. Worked example
Volume: 4000 m² × 3.0 m = 12,000 m³.
- Normal mode at 6 ach: 12,000 × 6 / 3600 = 20 m³/s (72,000 m³/h).
- Smoke clearance at 10 ach: 12,000 × 10 / 3600 ≈ 33.3 m³/s.
- IMC check: 3.8 l/s·m² × 4000 m² ≈ 15.2 m³/s.
Use two or more exhaust fans, for example 2 × 16.7 m³/s, so that one fan failure leaves half the capacity, with a separate standby where the authority requires it. In normal mode both fans run at about 60 % speed (flow is proportional to speed), which needs only about 0.6³ ≈ 22 % of full-speed power. With CO control they run lower or stop most of the day.
Make-up air of roughly 75 to 80 % of exhaust enters through ramps or dedicated shafts, located at the far end from the exhaust so the air sweeps the whole floor.
3. CO and NO₂ control
- Typical setpoints: low speed above about 25 to 30 ppm CO, high speed above about 50 ppm. As a reference, the EU occupational limit for CO is 20 ppm over 8 hours and 100 ppm for 15 minutes.
- Add NO₂ sensors where diesel vehicles park (typical stage around 1 to 3 ppm).
- Mount CO sensors at breathing height (about 1.5 to 1.8 m), at ramps, near exits and in dead corners, at the spacing given by the sensor’s coverage data.
- In fire mode the fire alarm overrides gas control.
4. Jet fan layout
- Place jet fans in series along the flow path towards the exhaust, clear of beams and services directly in front of the outlet, with their throw overlapping the next fan.
- Avoid blowing against the incoming make-up air or into dead-end bays without an exhaust point.
- Fire-mode fans and their cables must be rated for smoke temperature (EN 12101-3 classes such as F300 or F400, as the authority specifies) with secondary power supply.
- Verify smoke mode by CFD: visibility and temperature along escape routes and firefighting access, reversing the flow for different fire locations if the scheme requires it.
Common mistakes
- Sizing exhaust fans only for 6 ach while the fire strategy needs 10 ach.
- Make-up air entering right next to the exhaust.
- Too few CO sensors, or sensors near the ceiling or at the ramp mouth only.
- Ramps and bays with no air movement because jet fans ignore beam layout.
Related: Car Park Ventilation with Jet Fans: Quick Design. For deeper study: HVAC Systems Design Course.
Check the edition of the code that applies to your project.
-